Brian,
The numbers in the US Building codes should be considered as absolute
minimums.
In the 1960's, the US Dept of Housing and Urban Development issued some
guidelines for both STC and IIC in three grades of construction. Between
similar rooms in either luxury housing or housing in a quiet community, they
recommended 55. For more typical communities, 52, and for noisy
communities, 48. Higher ratings were recommended where rooms were
dissimilar such as a kitchen over a bedroom. In recent years, the trend
among consultants in North America is to recommend walls with higher
laboratory STC ratings, recognizing both the common field flanking problems
and the growth of high power music systems.
>I am trying to locate recommended IIC ratings (or equivalent) in buildings
>for various situations used around the world.
[quoted text clipped - 11 lines]
>
> Brian
abr@norconsult.no - 23 May 2005 12:28 GMT
Hello,
In Norway, the minimum requirements for dwellings is Rw'>=55dB and
Ln,w'<=53dB. Note that is FIELD measured values. In Sweden, I think is
Rw'50-5000>=55dB and L'n,w50-5000<=56dB. The swedish requirements take
into account low frequencies disturbance which typically occurs with
wood contruction. This is taken also in account in the norwegian
requirements but only as guidelines for improved sound insulation.
We use constructions with laboratory measurements 4 - 6 dB better the
field requirements. Fortunately, it has been done an extensive work
through the years by the Norwegian building research center to collect
field measurement datas made by theme selv and other concultants. The
results is a database giving expected field values for a great number
of different constructions. VERY usefull!
Alain Bradette
> Brian,
>
> The numbers in the US Building codes should be considered as absolute
> minimums.
>
[quoted text clipped - 23 lines]
> >
> > Brian
Brian Marston - 23 May 2005 13:23 GMT
In Australia the current floor/ceiling Ln,Tw+Ci value in our latest
Building Code is 62dB (as tested in the field).
As the Ci value is a -ve value, then removeing the +ci value leads to an
Ln,w value that is even higher. The equivalent IIC would be more likely
45 or less.
In the area of wall ratings at least our STC requirement has gone from
STC 45 to the equivalent of STC 55.
While agreeing that the building code values are minimum values, the
building industry takes these as the minimum/maximum that needs to be
achieved without any graduation (Grade I, Grade II, Grade III) as in the
HUD values.